no ground on electrical outlets in my apartment
#90363 04/14/05 02:07 PM
Joined: Mar 2002
Posts: 1,351
connoisseur
OP Offline
connoisseur
Joined: Mar 2002
Posts: 1,351
i'm quite sure this is rather serious:

There are absolutely no grounded outlets in the entire building and no ground wires anywhere. they also won't put any in as it's too pricey. There are a few 3 prong outlets, however, but they are just there, not grounded.

I have an axiom home theatre, a big screen tv and a laptop that I'm quite worried about. What I have done is I have a UPS plugged into the wall, and then a power bar off the UPS. I plug everything into the power bar.

1 - Is that enough protection (UPS then power bar) ?

2 - Would there be a way for me to ground one of these outlets?

3 - What events could cause problems due to the lack of ground? Static? Electrical storms? Spikes and dips in the voltage?

thanks very much for all replies
Ravi

Re: no ground on electrical outlets in my apartment
#90364 04/14/05 02:45 PM
Joined: Dec 2004
Posts: 540
aficionado
Offline
aficionado
Joined: Dec 2004
Posts: 540
it's kinda odd that your place doesn't have a grounding system. I didn't even think that was up to code anymore. What you probably ought to do is get a GFCI plug like this and then plug it in between the UPS and the power bar. I'm not that familiar with the specifics in the operation of the UPS so it's should probably go "downstream" of the UPS. Since your building isn't grounded, a mismatch between the incoming and outgoing current means either your equipment is getting zapped or you are. This device will detect it and then trip itself off, stopping all current flow and keep you from riding the lightning. Now these things are designed for a ground lead but it should still work for you. I'd check with the resident electrician wherever you buy it from.


Who's the more foolish, the fool or the fool who follows him?
Re: no ground on electrical outlets in my apartment
#90365 04/14/05 04:12 PM
Joined: Mar 2002
Posts: 1,351
connoisseur
OP Offline
connoisseur
Joined: Mar 2002
Posts: 1,351
Ash,

thanks for the suggestion

i have done a quick look up on them online. it seems to be a good idea.

my only question is, since there is an absence of a ground, will it always trip?

Re: no ground on electrical outlets in my apartment
#90366 04/14/05 04:15 PM
Joined: Apr 2003
Posts: 220
local
Offline
local
Joined: Apr 2003
Posts: 220
WOW!! Nice to know that I'm not the only one with this same problem. The house that I just bought does not have a ground in the living room where my HT will be. Also the outlets are 2 prong so that means that I can either change out the outlets to a 3 prong (no ground of course) or use adapters.

I do have a surge protector, but would the GFCI cord be a good addition to act as a ground?

Re: no ground on electrical outlets in my apartmen
#90367 04/14/05 05:27 PM
Joined: May 2003
Posts: 18,044
shareholder in the making
Offline
shareholder in the making
Joined: May 2003
Posts: 18,044
I use the cheater plugs and actually screw them to the center screw (or outer screws, if necessary) on the important outlets. I thought it was law that they had to provide grounded 3 prongs in the bathrooms at least.


I am the Doctor, and THIS... is my SPOON!
Re: no ground on electrical outlets in my apartmen
#90368 04/14/05 05:34 PM
Joined: Jan 2002
Posts: 1,459
Likes: 6
connoisseur
Online Content
connoisseur
Joined: Jan 2002
Posts: 1,459
Likes: 6
That does not mean that you are grounded.

I beleive the law in Canada is any outlet near water requires GFI plugs.
Not sure about other countries like the US or Quebec. ;-P



Re: no ground on electrical outlets in my apartmen
#90369 04/14/05 05:51 PM
Joined: Mar 2002
Posts: 1,351
connoisseur
OP Offline
connoisseur
Joined: Mar 2002
Posts: 1,351
kcarlile

i don't think a cheater plug actually grounds anything. it's just meant to reverse polarity.

Re: no ground on electrical outlets in my apartmen
#90370 04/14/05 05:52 PM
Joined: May 2003
Posts: 18,044
shareholder in the making
Offline
shareholder in the making
Joined: May 2003
Posts: 18,044
Well, the power strips that have ground fault lights say that it's OK, and I figure it's better than nothing. (The lights do go on when they're not screwed into the outlets, so...)


I am the Doctor, and THIS... is my SPOON!
Re: no ground on electrical outlets in my apartmen
#90371 04/14/05 06:00 PM
Joined: Mar 2002
Posts: 1,351
connoisseur
OP Offline
connoisseur
Joined: Mar 2002
Posts: 1,351
I wonder if it will actually protect

does anyone know what happens exactly if you don't have a ground? what can happen to your equipment? what events can cause a negative effect?

Re: no ground on electrical outlets in my apartmen
#90372 04/14/05 07:00 PM
Joined: Dec 2004
Posts: 540
aficionado
Offline
aficionado
Joined: Dec 2004
Posts: 540
basically, without a ground wire in the wall connected to the outlet, if your equipment were to short to the casing there would NOT be a complete path to ground for the electricity. this would result in the casing being as the same voltage as whatever was faulted (ex. a power supply cord shorted to case=120VAC) so if you went to touch it you get painfully tingly. also it could present a fire hazard if something flammable was touching it. now with a grounding wire installed in the plug, the flow path of electricity would be from the fault to the case, through the ground wire in the power cord (the bottom center, round conductor) through the ground wire in the outlet, to the house's common ground, and then literally to the ground. i can come up with a picture when i get home if you'd like, i'm at work now. you know, i'm glad this topic came up. i finally get to use some of my 6 years of electrical experience in the Navy!


Who's the more foolish, the fool or the fool who follows him?
Re: no ground on electrical outlets in my apartmen
#90373 04/14/05 07:06 PM
Joined: Mar 2002
Posts: 1,351
connoisseur
OP Offline
connoisseur
Joined: Mar 2002
Posts: 1,351
Ash
thanks so much, that post completely explained the use of ground to me.

Re: no ground on electrical outlets in my apartmen
#90374 04/14/05 08:50 PM
Joined: Dec 2004
Posts: 540
aficionado
Offline
aficionado
Joined: Dec 2004
Posts: 540
glad to hear it! i wasn't lookin forward to figuring out how to draw the picture in Word!!


Who's the more foolish, the fool or the fool who follows him?
Re: no ground on electrical outlets in my apartmen
#90375 04/15/05 03:46 PM
Joined: Jan 2002
Posts: 1,459
Likes: 6
connoisseur
Online Content
connoisseur
Joined: Jan 2002
Posts: 1,459
Likes: 6
That is interesting.....

Perhaps the electrical box IS grounded, but this ground was not connected to the outlet. Have you checked the wiring to see if it does/doesn't have a ground wire?

I might also venture that the electrical box and associated connection to the wall provides enough resistance to "trick" the powerbar into a grounded state.

Sorry, the electrical engineer in my coming out!!!!

Re: no ground on electrical outlets in my apartmen
#90376 04/15/05 04:30 PM
Joined: Dec 2004
Posts: 540
aficionado
Offline
aficionado
Joined: Dec 2004
Posts: 540
In reply to:

I might also venture that the electrical box and associated connection to the wall provides enough resistance to "trick" the powerbar into a grounded state.


the box is probably anchored to a wooden stud or else just in the drywall. either way, i think it'd be too high a resistance for the powerbar to register it as grounded. of course, it could be a steel framed building, in which case the box might be grounded.


Who's the more foolish, the fool or the fool who follows him?
Re: no ground on electrical outlets in my apartmen
#90377 04/15/05 04:46 PM
Joined: May 2003
Posts: 18,044
shareholder in the making
Offline
shareholder in the making
Joined: May 2003
Posts: 18,044
Oh, I don't have anywhere near the experience to do that! I just kind of assumed it would work, because all of those things have little wires or screw holes on them. I'm just going to stick my fingers in my ears and go "la la la la it's safe la la la la!"


I am the Doctor, and THIS... is my SPOON!
Re: no ground on electrical outlets in my apartmen
#90378 04/15/05 04:59 PM
Joined: Jan 2004
Posts: 3,016
B
connoisseur
Offline
connoisseur
B
Joined: Jan 2004
Posts: 3,016
In reply to:

Oh, I don't have anywhere near the experience to do that! I just kind of assumed it would work...



...but i did stay at a Holiday Inn Express last night!!



bigjohn


EXCUSE ME, ARE YOU THE SINGING BUSH??
Re: no ground on electrical outlets in my apartmen
#90379 04/15/05 07:25 PM
Joined: May 2003
Posts: 18,044
shareholder in the making
Offline
shareholder in the making
Joined: May 2003
Posts: 18,044
Wha?

I have TiVo. I know not of what you speak.

Neener neener.


I am the Doctor, and THIS... is my SPOON!
Re: no ground on electrical outlets in my apartmen
#90380 04/15/05 07:32 PM
Joined: Jan 2004
Posts: 3,016
B
connoisseur
Offline
connoisseur
B
Joined: Jan 2004
Posts: 3,016
i guess i am 'old school'.. i still watch commercials

bigjohn


EXCUSE ME, ARE YOU THE SINGING BUSH??
Re: no ground on electrical outlets in my apartmen
#90381 04/15/05 08:17 PM
Joined: Jul 2004
Posts: 828
aficionado
Offline
aficionado
Joined: Jul 2004
Posts: 828
bjohn your not old school. my mom is old schoold she did not watch comercials "thats why i have kids" watching tv with my mother was tiring. lol


------------------------------------------------
Leave the gun, Take the canolis.
Re: no ground on electrical outlets in my apartmen
#90382 04/15/05 08:23 PM
Joined: Jan 2004
Posts: 3,016
B
connoisseur
Offline
connoisseur
B
Joined: Jan 2004
Posts: 3,016
i remember the days when i was the remote. my dad had this big old curtis mathis TV. it used to sound like the space shuttle powering up when you turned it on.

had the 2 big rotary dials on the upper right hand side. and when you would turn that dial, it would go, "KA-Chunkt, Ka-Chunkt, Ka-Chunkt"...

ah, the memories!!

bigjohn


EXCUSE ME, ARE YOU THE SINGING BUSH??
Re: no ground on electrical outlets in my apartmen
#90383 04/15/05 08:31 PM
Joined: Jul 2004
Posts: 828
aficionado
Offline
aficionado
Joined: Jul 2004
Posts: 828
it started out as a dial but eventually turned into vicegrips or plyers.


------------------------------------------------
Leave the gun, Take the canolis.
Re: no ground on electrical outlets in my apartmen
#90384 04/15/05 10:00 PM
Joined: Apr 2003
Posts: 608
aficionado
Offline
aficionado
Joined: Apr 2003
Posts: 608
if the wire has a metal outer coating and is connected to a metal electrical box in the wall,the metal is the ground-its called bx cable,used mostly in commercial applications and some older houses

Page 1 of 3 1 2 3

Moderated by  alan, Amie, Andrew, axiomadmin, Brent, Debbie, Ian, Jc 

Link Copied to Clipboard

Need Help Graphic

Forum Statistics
Forums16
Topics24,940
Posts442,457
Members15,616
Most Online2,082
Jan 22nd, 2020
Top Posters
Ken.C 18,044
pmbuko 16,441
SirQuack 13,840
CV 12,077
MarkSJohnson 11,458
Who's Online Now
0 members (), 145 guests, and 4 robots.
Key: Admin, Global Mod, Mod
Newsletter Signup
Powered by UBB.threads™ PHP Forum Software 7.7.4