ABCs of APC UPSs
|
Joined: Sep 2004
Posts: 11,458
shareholder in the making
|
OP
shareholder in the making
Joined: Sep 2004
Posts: 11,458 |
Huh? Anyway, I'm a big user of UPS units... I literally have probably 12 or so in use and another 3-4 down in my workshop with a need for replacements. ALL of them are APC units, and almost all of them are ~1100 ~ 1200 units, purchased at Sam's Club, etc... NOT from a "pro" or "Server" line. I'm beginning to wonder about the quality of them. It seems as though when I buy a unit, I only get maybe a year and a half to two years tops out of it before the "battery warning" starts buzzing and letting me know it needs a replacement. And when the batteries run ~$120 or so, I typically feel like I might as well buy a whole new unit for ~$180 instead. Have any of you IT people in the "know" been hearing anything about UPS units and lifespan, quality, etc.? I just hauled one out of my office because it was putting out a stink like burning hair or like it just went to the salon and got a perm! I've smelled something similar once when a capacitor blew in a flash head. It was hot as hell, too. I put it out on my back porch an hour ago, and I still can't touch the bottom metal plate. At least nothing caught fire. Yet. I think I need a new one ASAP!
::::::: No disrespect to Axiom, but my favorite woofer is my yellow lab :::::::
|
|
|
Re: ABCs of APC UPSs
|
Joined: Apr 2003
Posts: 16,441
shareholder in the making
|
shareholder in the making
Joined: Apr 2003
Posts: 16,441 |
I'm pretty sure we had an approx. 2 year replacement cycle on APC UPS batteries back when I was responsible for the servers that were plugged into them.
|
|
|
Re: ABCs of APC UPSs
|
Joined: Sep 2004
Posts: 11,458
shareholder in the making
|
OP
shareholder in the making
Joined: Sep 2004
Posts: 11,458 |
So you're thinking that this might just be typical? Maybe I'm expecting too much in assuming that the lead acid batteries in there should be good for 4 years, like all the ones I used to use for portable lights in video production or like a car battery?
::::::: No disrespect to Axiom, but my favorite woofer is my yellow lab :::::::
|
|
|
Re: ABCs of APC UPSs
|
Joined: Feb 2009
Posts: 3,466
connoisseur
|
connoisseur
Joined: Feb 2009
Posts: 3,466 |
The way the UPS uses the battery is what cuts its life in half. Because the UPS wants to deliver a maximum run time in the event of power failure the battery is always topped off. Normal use of a battery is to run it down quite a bit before charging it again.
I was looking at a PurePower UPS, which is intended for home theater use (and has a price tag which gives away that intention). One nice thing about is it does periodically run on battery to attempt to keep the cells conditioned.
Pioneer PDP-5020FD, Marantz SR6011 Axiom M5HP, VP160HP, QS8 Sony PS4, surround backs -Chris
|
|
|
Re: ABCs of APC UPSs
|
Joined: May 2003
Posts: 18,044
shareholder in the making
|
shareholder in the making
Joined: May 2003
Posts: 18,044 |
2 years. Uh huh. Unless you're talking about different ones than the ones I inherited, Peter, it was more like 6-8 years. That's actually about the point where I generally see them fail. Mark, are you using Smart-UPS or Back-UPS? Smart-UPS seem to last a lot longer.
I am the Doctor, and THIS... is my SPOON!
|
|
|
Re: ABCs of APC UPSs
|
Joined: Sep 2004
Posts: 11,458
shareholder in the making
|
OP
shareholder in the making
Joined: Sep 2004
Posts: 11,458 |
Hmmmm... all the ones immediately around me are Back-UPS....
::::::: No disrespect to Axiom, but my favorite woofer is my yellow lab :::::::
|
|
|
Re: ABCs of APC UPSs
|
Joined: May 2003
Posts: 18,044
shareholder in the making
|
shareholder in the making
Joined: May 2003
Posts: 18,044 |
Ah yeah, those things die quickly.
I am the Doctor, and THIS... is my SPOON!
|
|
|
Re: ABCs of APC UPSs
|
Joined: Dec 2007
Posts: 7,786
axiomite
|
axiomite
Joined: Dec 2007
Posts: 7,786 |
Interesting. The ups units in our plant are all APC and are between 3 and 5 years old. We had the first two fail this year (one today).
Fred
------- Blujays1: Spending Fred's money one bottle at a time, no two... Oh crap!
|
|
|
Re: ABCs of APC UPSs
|
Joined: Sep 2004
Posts: 11,458
shareholder in the making
|
OP
shareholder in the making
Joined: Sep 2004
Posts: 11,458 |
I'll probably end up with an APC because I'll need something sooner rather than later, and they're so widely available. And, I probably WON'T get the SMART UPS line, because I'll just have a hard time convincing Joyce (and myself too, I guess) that they're worth being more than double the cost...
I guess this has still been helpful as no one has said unequivocally that APC brand units have reliability issues.
::::::: No disrespect to Axiom, but my favorite woofer is my yellow lab :::::::
|
|
|
Re: ABCs of APC UPSs
|
Joined: May 2003
Posts: 18,044
shareholder in the making
|
shareholder in the making
Joined: May 2003
Posts: 18,044 |
Are you doing the Trade-UPS program? Might knock a little bit off the cost.
I am the Doctor, and THIS... is my SPOON!
|
|
|
Re: ABCs of APC UPSs
|
Joined: Sep 2004
Posts: 11,458
shareholder in the making
|
OP
shareholder in the making
Joined: Sep 2004
Posts: 11,458 |
Hmmmm.. I'm not familiar with it. Thanks, I'll look into it!
::::::: No disrespect to Axiom, but my favorite woofer is my yellow lab :::::::
|
|
|
Re: ABCs of APC UPSs
|
Joined: Dec 2007
Posts: 7,786
axiomite
|
axiomite
Joined: Dec 2007
Posts: 7,786 |
Speaking of failing batteries... Is there any way to test, or tell if a battery is close to failing?
I can just wait and every time a production computer crashes due to power outage, but I prefer a more elegant solution.
Fred
------- Blujays1: Spending Fred's money one bottle at a time, no two... Oh crap!
|
|
|
Re: ABCs of APC UPSs
|
Joined: May 2003
Posts: 18,044
shareholder in the making
|
shareholder in the making
Joined: May 2003
Posts: 18,044 |
There should be some sort of management interface you can use; there's also the test button on the UPS--whatever that does. You could always just unplug it from the wall...
I am the Doctor, and THIS... is my SPOON!
|
|
|
Re: ABCs of APC UPSs
|
Joined: Sep 2004
Posts: 11,458
shareholder in the making
|
OP
shareholder in the making
Joined: Sep 2004
Posts: 11,458 |
The way the UPS uses the battery is what cuts its life in half. Because the UPS wants to deliver a maximum run time in the event of power failure the battery is always topped off. Normal use of a battery is to run it down quite a bit before charging it again.
To the best of my knowledge (and I'm pretty sure about this), this is NOT a good idea with lead acid batteries. NiCad, definitely, and nickel metal hydride & li-ion sometimes, depending upon use patterns and "memory" issues.
::::::: No disrespect to Axiom, but my favorite woofer is my yellow lab :::::::
|
|
|
Re: ABCs of APC UPSs
|
Joined: May 2003
Posts: 2,185
connoisseur
|
connoisseur
Joined: May 2003
Posts: 2,185 |
As an engineer who uses a lot of rechargeable batteries and replaced my Macbook battery 4x, I should've realized this. My APC UPS beeped years ago after about 5 years of use. It never occurred to me that it was the battery. I just stopped using that block of plugs out of sheer laziness.
Are there any reasonably priced UPS's that have a replaceable battery? Or are home users just expected to buy new ones every few years? That'd be a waste.
|
|
|
Re: ABCs of APC UPSs
|
Joined: May 2003
Posts: 18,044
shareholder in the making
|
shareholder in the making
Joined: May 2003
Posts: 18,044 |
They're replaceable. Just expensive.
I am the Doctor, and THIS... is my SPOON!
|
|
|
Re: ABCs of APC UPSs
|
Joined: May 2003
Posts: 2,185
connoisseur
|
connoisseur
Joined: May 2003
Posts: 2,185 |
I should've said is there a type that has 'reasonable' replacement batteries or does it end up costing the same buying new ones?
|
|
|
Re: ABCs of APC UPSs
|
Joined: Dec 2007
Posts: 7,786
axiomite
|
axiomite
Joined: Dec 2007
Posts: 7,786 |
There should be some sort of management interface you can use; there's also the test button on the UPS--whatever that does. You could always just unplug it from the wall... I do the unplug thing every once in a while, but I know I checked the one that failed today when the first one failed and it showed no problems. I noticed the computer connection on the new ones today. Guess I have something to check out at work Tomorrow night.
Fred
------- Blujays1: Spending Fred's money one bottle at a time, no two... Oh crap!
|
|
|
Re: ABCs of APC UPSs
|
Joined: Sep 2004
Posts: 11,458
shareholder in the making
|
OP
shareholder in the making
Joined: Sep 2004
Posts: 11,458 |
Is it ever recommended to just apply a load to these (say, a 60 watt bulb) and just let them run down occasionally (NOT down to the point of -0- amperage, but just down to, say, 15%)?
::::::: No disrespect to Axiom, but my favorite woofer is my yellow lab :::::::
|
|
|
Re: ABCs of APC UPSs
|
Joined: Nov 2006
Posts: 1,333
connoisseur
|
connoisseur
Joined: Nov 2006
Posts: 1,333 |
It's been hit or miss with our units at work. We've had some on line for 6+ years without a hickup and we've had others that lasted about a year including a HUGE APC unit with 2 - 20 Amp circuits that will run over an hour at full load! The batteries on that unit died about a week after the warranty expired. I got replacement batteries from Planet Battery and it's been fine for several years now. Scott
|
|
|
Re: ABCs of APC UPSs
|
Joined: Sep 2004
Posts: 11,458
shareholder in the making
|
OP
shareholder in the making
Joined: Sep 2004
Posts: 11,458 |
Thanks, Scott! As I mentioned, I've got a few UPS units sitting in my basement, needing a battery change. I'm going to check into that trade-ups program a bit more to see what I can get for them in comparison to replacing the batteries, but have a question:
I've read before that some types of spike protectors actually "wear out" over time... Does anyone know if this applies to UPS units?
In short: If I replace a battery in a two year old UPS, is it as good as new? This would likely determine whether I replace the batts in the ones downstairs or trade them in.
BTW, this is my 5,000th post. I feel an incredibly overwhelming desire to call Jack old, JP crazy, or at least make a fart or booby joke to mark the occasion.
::::::: No disrespect to Axiom, but my favorite woofer is my yellow lab :::::::
|
|
|
Re: ABCs of APC UPSs
|
Joined: Nov 2006
Posts: 1,333
connoisseur
|
connoisseur
Joined: Nov 2006
Posts: 1,333 |
Hi Mark,
We have UPS's all over the place at work, but I've only had one at home. I think we took a lightning strike , because one night during a storm, it fried; I mean, the blue smoke got out and everything. It was the only electronic hardware that was effected that night. After that, it only passed 120VAC, but no battery and no surge protection. Basically it was an expensive, but short, extension cord. Since then, I have not used one at home. Maybe I should, considering our iMac is considerably more expensive than a small UPS...
I do have Brick Wall units on my AV equipment, but no battery back-up.
Scott
|
|
|
Re: ABCs of APC UPSs
|
Joined: Sep 2004
Posts: 11,458
shareholder in the making
|
OP
shareholder in the making
Joined: Sep 2004
Posts: 11,458 |
I know it's a bit rude to bump my post, but I wonder if it was a matter of no one seeing it or no one having an answer. Besides, it's not about Bose or Apple or Religion or Politics:
~~~~~~~~~~~ I've read before that some types of spike protectors actually "wear out" over time... Does anyone know if this applies to UPS units?
In short: If I replace a battery in a two year old UPS, is it as good as new? This would likely determine whether I replace the batts in the ones downstairs or trade them in. ~~~~~~~~~~~
Anyone? Pretty please? I've got 5 UPS units to decide this with...!
::::::: No disrespect to Axiom, but my favorite woofer is my yellow lab :::::::
|
|
|
Re: ABCs of APC UPSs
|
Joined: May 2003
Posts: 18,044
shareholder in the making
|
shareholder in the making
Joined: May 2003
Posts: 18,044 |
Wish I knew the answer to that, Mark.
I am the Doctor, and THIS... is my SPOON!
|
|
|
Re: ABCs of APC UPSs
|
Joined: Sep 2004
Posts: 11,458
shareholder in the making
|
OP
shareholder in the making
Joined: Sep 2004
Posts: 11,458 |
Well, thanks for looking! Come again!
::::::: No disrespect to Axiom, but my favorite woofer is my yellow lab :::::::
|
|
|
Re: ABCs of APC UPSs
|
Joined: May 2003
Posts: 18,044
shareholder in the making
|
shareholder in the making
Joined: May 2003
Posts: 18,044 |
I think the surge protectors wearing out has to do with them only lasting through one spike. I would suspect that if UPSes deal with simliar spikes in similar ways, they'd also wear out. But if the fans still work on the UPSes, they only complain about the battery, and if you put a new battery in they cease complaining, they're still good. But I'm really not sure.
I am the Doctor, and THIS... is my SPOON!
|
|
|
Re: ABCs of APC UPSs
|
Joined: Aug 2009
Posts: 93
old hand
|
old hand
Joined: Aug 2009
Posts: 93 |
I've read before that some types of spike protectors actually "wear out" over time... Does anyone know if this applies to UPS units?
In short: If I replace a battery in a two year old UPS, is it as good as new? This would likely determine whether I replace the batts in the ones downstairs or trade them in.
Mark: I'm an electronics technician and at one time I did bench repair for a company that made industrial UPS's for the cable television industry. To my knowledge there is nothing in a UPS that would wear out. A UPS basically senses voltage and switches to the battery and voltage inverter to create AC when the voltage drops below a set threshold. They are pretty simple circuits all in all. The only thing I could think of that would remotely wear out are the capacitors but modern caps are robust and don't dry out like the old caps did. I don't remember ever having replaced parts on a UPS because they wore out. Unless the UPS's have taken a lightning hit, I would just replace the batteries. The UPS you mentioned that has the electronics stink probably did fry and I wouldn't bother replacing the battery in it. I'm not familiar with the UPS's you have but the ones I repaired just used a standard motorcycle battery. Maybe you can source a cheaper battery for yours if you look around? Good luck, Joe
Last edited by jollo; 10/16/09 11:22 PM. Reason: batteries
|
|
|
Re: ABCs of APC UPSs
|
Joined: Sep 2004
Posts: 11,458
shareholder in the making
|
OP
shareholder in the making
Joined: Sep 2004
Posts: 11,458 |
Thanks, Joe! I appreciate the reply!
I think it was surge suppressors that used Metal-Oxide something or another that I read "wear out" over time....
::::::: No disrespect to Axiom, but my favorite woofer is my yellow lab :::::::
|
|
|
Re: ABCs of APC UPSs
|
Joined: Aug 2009
Posts: 93
old hand
|
old hand
Joined: Aug 2009
Posts: 93 |
Mark: Here is interesting read on surge protectors if you are interested: Surge protectors. What you are asking about is a MOV (metal oxide varistor) that will shunt spikes and or surges and you are right they can burn out with a good enough surge. I didn't think about surge protection because the UPS's I repaired didn't have any (the cable companies used a separate industrial grade dedicated surge protector in front of the UPS's), sorry about that. I found the schematics for an APC 1200 and had a look, they do use MOV's on the input and they don't show the ratings just a part number so I'm not sure how big a spike they can handle before they need replacing.
Last edited by jollo; 10/17/09 12:18 AM.
|
|
|
Re: ABCs of APC UPSs
|
Joined: Dec 2007
Posts: 7,786
axiomite
|
axiomite
Joined: Dec 2007
Posts: 7,786 |
Anyone? Pretty please? I've got 5 UPS units... I'll see your 5 UPS units and raise you a Bose. ::puts on best poker face::
Fred
------- Blujays1: Spending Fred's money one bottle at a time, no two... Oh crap!
|
|
|
Re: ABCs of APC UPSs
|
Joined: Apr 2007
Posts: 4,877
connoisseur
|
connoisseur
Joined: Apr 2007
Posts: 4,877 |
Bought a new APC UPS today. I have been having problems lately.. at least once every day or two everything plugged into my old APC battery unit would shut down (receiver, TV, ps3, ect.) and then come right back on. This would happen in the middle of a movie or game and was really annoying (not to mention probably bad for my electronics). The old one was only rated at 500VA/300W and was about 4-5 years old. I suspect that the Power strip was causing the problems (breakers never flipped in the back room). Hopefully this won't happen anymore with the new APC. It also looks pretty freaking cool with the lighted info screen. I bought an APC 1500VA 865 Watt unit. It was on sale at staples for $169.99. Also, as a bonus it has a power save feature that allows me to plug my receiver into the "Master" input and my subwoofer into the "Secondary" input so that my ep500 shuts off when my receiver is turned off. I haven't took effort to hook a 12 v trigger cable up to my ep500 and denon so it is nice to finally let my sub power off.
-David
|
|
|
Re: ABCs of APC UPSs
|
Joined: Sep 2004
Posts: 11,458
shareholder in the making
|
OP
shareholder in the making
Joined: Sep 2004
Posts: 11,458 |
I was looking at those the other day, as I received an advance Staples flyer that showed all APC UPS units on sale... That's a pretty decent price on it and will likely pick one up tomorrow as well! Thanks, David!
::::::: No disrespect to Axiom, but my favorite woofer is my yellow lab :::::::
|
|
|
Re: ABCs of APC UPSs
|
Joined: Apr 2007
Posts: 4,877
connoisseur
|
connoisseur
Joined: Apr 2007
Posts: 4,877 |
No problem. With my 50" LCD rp, denon 3808, and PS3 hooked up to the battery supply the most I am pulling is about 450 watts when playing an online mulitplayer game on the ps3. My ep500 is also plugged in, but not into one of the 5 battery enabled outlets so I don't think that the wattage displayed includes that. This is at typical listening levels, with my DVR on in the background as well. IF I have my xbox360 running in the background you can add about 100 more watts. Battery run time is about 12 minutes in the above scenario.
-David
|
|
|