Quote:

On the panels I've seen- there are white/Neutral buses down each side (for all white wires only). The bare ground wires have their own bus on one side or the other. These should be separate as Jakewash said. *** So, not only should the white and bare wires not share the same screw, they should not share the same bus either ***.


Correct... there is a neutral bus bar and a ground bar, ne'er the t'wain shall meet (except through the neutral bond).

If you do have neutral and ground wires on the same bus bar, you do have a problem. No matter how nice your builder's office is and how expensive the salesman's suit was, something went wrong.

Bren R.